No, a ground is not required for a GFCI (Ground Fault Circuit Interrupter) outlet to work. GFCIs work by detecting imbalances in the current between the hot and neutral wires, and will trip the circuit if there's an imbalance. However, there are some disadvantages to installing GFCI outlets without a ground wire:A GFCI requires a ground wire. If there is no ground the GFCI (ground fault circuit interrupter) will detect a ground fault and interrupt the circuit... i.e. trip immediately.
You will need to figure out some way to run a ground wire to the outlet... and every subsequent outlet on the circuit. Without a ground wire to every outlet on the circuit a GFCI is useless... it wouldn't be giving any protection even if you did get it to not trip.
You can look up the current codes but I am pretty sure metal conduit can no longer be used for grounding outlets. If there is metal conduit from the box to the panel you might be able to tie a string to the current cable, pull the current cable out then use the string to pull a 3 conductor cable with a proper integrated ground. If there is conduit end to end you can pull 3 THHN wires (black, white, green) instead of a cable (Romex) if you prefer... individual wires are usually much easier to pull through conduit than a cable (Romex).